Skip to main content

BACnet

This document explains how to connect BACnet devices to Aqara Studio.

Prerequisites

Before you start, please make sure your network meets these conditions based on your device type:

  • For BACnet/IP devices: The BACnet/IP device, Aqara gateway, and your computer must be on the same local area network (LAN).
  • For BACnet MS/TP devices: The BACnet MS/TP device is already connected to a BACRouter, and the BACRouter, Aqara gateway, and your computer are all on the same LAN.

Add A BACnet Device

  1. Click the Devices page in the left sidebar. In the device tree on the left, click the “+” button.
    Click the addition button

  2. In the popup, choose BACnet IP.
    Select Bacnet IP

  3. Select BACnet IP. Go to the Protocol Configuration tab, and set the protocol parameters.

    Configure Protocol

    The relevant parameters are shown in the following table:

    CategoryParameterRequiredDescriptionExample
    Basic ConfigurationNetwork NumberIt identifies the logical subnet, and must be unique. Range: [0, 65535].
    • 0: Local network
    • 65535: Broadcast network
    1
    UDP PortThe UDP port for BACnet/IP communication. Default is 47808 (0xBAC0).47808
    Local IP AddressThe IP address of the device on which Aqara Studio is deployed. Format: xxx.xxx.xxx.xxx (for example, 192.168.1.100). Default is 0.0.0.0, which allows the system to assign it automatically.1
    Device Object Instance NumberA unique identifier for the BACnet device on the BACnet network. Range: [0, 4194303].1
    Worker Mode ConfigurationBACnet/IP Device TypeThe following options are supported:
    • Standard Device: General BACnet devices (such as controllers, servers, clients) that use UDP port 47808 (default).
    • Foreign Device: Not on the local subnet, must be registered with BBMD to enable cross-subnet communication.
    • Broadcast Management Device (BBMD): Manages foreign device registration, forwards broadcast messages, and maintains the broadcast table.
    Standard Device
    BBMD UDP PortThe listening port for BBMD services, default is 47808. Required if the BACnet/IP device mode is Foreign Device or Broadcast Management Device.47808
    BBMD IP AddressThe IP address of the BBMD. This is the target for foreign device registration and is used for cross-subnet broadcasts. Required if device mode is Foreign Device or Broadcast Management Device.null
    Advanced ConfigurationMax APDU Length Accepted (bytes)The maximum supported APDU (Application Protocol Data Unit) length in bytes. It is recommended to set no larger than 1476.1076
    Segmentation SupportedOptions:
    • Segmented Both (default): The device supports segmented APDU messages both for sending and receiving.
    • Segmented Transmit: Only supports sending segmented messages.
    • Segmented Receive: Only supports receiving segmented messages.
    • No Segmentation: Does not support segmented messages. Only messages within the max APDU length are supported.
    Segmented Both
    APDU Segment TimeoutThe timeout for waiting for a segment acknowledgment when transmitting segmented APDU. Default is 2000ms.2s
    APDU TimeoutApplies only for non-segmented APDU transfers. Defines how long to wait for a response (such as ACK or Error). Default is 30000ms.30s
    Character SetThe character set used, to ensure text information can be correctly encoded and decoded between devices. Supported options: ISO_10646_UTF8, IBM_MICROSOFT_DBCS, JIS_X0208, ISO_10646_UCS4, ISO_10646_UCS2, ISO_8859_1, UNKNOWN.ISO_10646_UTF8
    Enable/Disable NetworkNote: If disabled, devices on this network will not work.-
  4. (Optional) Go to the "Add Device" tab, and click the ⚙ button to set up device discovery rules.

    Configure Protocol

    The relevant parameters are described in the following table:

    Field NameDescription
    Device objectId ≥Search for devices with instance numbers greater than or equal to this value. Minimum is 0.
    Device objectId ≤Search for devices with instance numbers less than or equal to this value. Maximum is 4194302.
    Network Instance FilterControl which network numbers to discover, such as 1,2,3,4. Default is all.
    Wait Response TimeThe time for the discovery process, in seconds.
    Note: If device discovery fails or some devices are not found, adjust this field based on network conditions.
  5. Click the “Discover Devices” button. Aqara Studio will then scan the network to find devices.

    tip

    If Aqara Studio does not find your BACnet device, you can also add the device manually.

    Discover Devices

  6. Select the device(s) you want to add, and click the "+" button in the center. The newly added device(s) will appear in the Added Device List on the right, and will also be displayed under BACnet IP in the device tree on the left.

    Add a Bacnet device

Add Points

  1. In the device tree, select the newly added device, go to the Point tab and click the Add point button.

    Bacnet Point Page

  2. In the "Add point" page, click Discover Points button, Aqara Studio will begin scanning to discover function points for this device.

    tip

    If the system does not discover the function points you need, you can also add them manually.

    Add points

  3. Select the required points and click the blue "+" button. The newly added points will appear in the Added Points list on the right, and will also be displayed under the related device in the device tree on the left.

    Aqara Studio will automatically map the points of BACnet devices to the feature points in the Aqara Spec protocol accordingly, enabling standardized control and management.

    tip

    If Aqara Studio mapped a point type incorrectly, you can select the point in the device tree, go to the Point detail page, and click Point Type to adjust it.

    Modify feature point type

Next Steps

Now, you can view details and control the device, or use the device in automation.

FAQ

How to Handle BACnet Devices Not Discovered by Aqara Studio

If Aqara Studio does not find your BACnet device, click "Manually Add." In the "Add Device" popup, enter the required parameters to finish adding the device.

Details for each parameter are as follows:

ParameterRequiredDescriptionExample
Device NameYour custom name for the BACnet device.
Device Object Instance NumberUnique ID for the BACnet device on the BACnet network. Range: [0, 4194303].1
Network NumberIdentifies the logical subnet, must be unique. Range: [0,65535]. 0: Local, 65535: Broadcast1
MAC AddressMAC address of the device.-
Address TypeSpecify the format and protocol type of MAC address:
  • UNKNOWN: Unknown type
  • ETHERNET: 6-byte Ethernet MAC, format AA:BB:CC:DD:EE:FF
  • IP: 4-6 byte IP address, format 192.168.1.1:47808
  • MSTP: 1 byte, Master-Slave/Token-Passing
  • SC: 6-byte Secure Connection, WebSocket
-
Max APDU Length Accepted (bytes)The maximum APDU (Application Protocol Data Unit) length in bytes. Recommended no larger than 1476.1076
Segmentation SupportedOptions:
  • Send and Receive Segmentation (default): Supports both sending and receiving segmented APDUs.
  • Send Only: Only supports sending segmented messages.
  • Receive Only: Can only receive segmented messages.
  • No Segmentation: Only unsegmented messages within the length limit are supported.
Send and Receive Segmentation
EncodingCharacter encoding used. Supported:
  • ISO_10646_UTF8
  • IBM_MICROSOFT_DBCS
  • JIS_X0208
  • ISO_10646_UCS4
  • ISO_10646_UCS2
  • ISO_8859_1
  • UNKNOWN
ISO_10646_UTF8
Vendor NameName of the device manufacturer.-
Model NameModel name of the device.-
Protocol RevisionEnter the Protocol_Revision property from BACnet.-
Firmware VersionEnter the Firmware_Revision property from BACnet.-
Application Software VersionEnter the Application_Software_Version property from BACnet.-

How to Handle BACnet Points Not Discovered by Aqara Studio

If Aqara Studio does not find the points you need, click "Manually Add" on the Point Add page, and enter the point parameters in the popup.

Details for each parameter are as follows:

ParameterRequiredDescription
Point NameYou can set a custom name for this point.
Aqara Object TypeObject type defined by Aqara.
Object TypeObject type as defined by BACnet.
Object Instance identifierThe instance number for this point. Range: [0, 4194303].